I know it's illegal to run general purpose stranded speaker wire inside a wall. Is it ok to run it inside a wall if it's inside metal conduit?
 

·
Registered
Joined
·
97 Posts
Discussion Starter #3
Thanks for the reply. Are you saying it’s illegal, or it’s not a good idea? I know it’s not a good idea and that’s why I’m asking. I have hundreds of dollars invested in some very heavy gage speaker wire for several long runs and that’s why I need to know if it’ll be legal if I run it inside metal conduit.
 

·
HTS Senior Moderator
Joined
·
5,288 Posts
It's against code. The reason however is for smoke toxicity. The in-wall rated cable has special jacket that will not produce noxious fumes when burned. Nothing to do whatsoever with electrical safety.

If you put it in metal conduit, you'll be fine and will be adhering to code.
 

·
Registered
Joined
·
97 Posts
Discussion Starter #5
Thanks again Bryan.

I knew it was because of the fumes given off and that’s why I thought it would be ok running inside conduit. Just wanted to make sure it was legal. I know I can’t use it to go from one floor to the next no matter what.
 